1.

A 10 MVA, 13.8 kV alternator has positive, negative and zero sequence reactances of 30%, 40% and 5% respectively. The value of resistance that must be placed in the generator neutral so that the fault current for a LG fault of zero fault impedance will not exceed the rated line current is ________Ω.18.43

Answer» A 10 MVA, 13.8 kV alternator has positive, negative and zero sequence reactances of 30%, 40% and 5% respectively. The value of resistance that must be placed in the generator neutral so that the fault current for a LG fault of zero fault impedance will not exceed the rated line current is ________Ω.
  1. 18.43