A three-phase star connected load consumes 600 W from a three-phase balanced supply. If the load is now re-connected in delta and fed from the same supply, the power consumption will be, 600 W 200 W 1.8 kW None of the aboveTell the ans of this question guys. |
|
Answer» : A three-phase star connected load consumes 600 W from a three-phase BALANCED supply. load is now re-connected in delta and FED from the same supply, To Find : the power consumption600 W200 W1.8 KW None of the aboveSolution:Power consumed by three IDENTICAL phase LOADS connected in delta is equal to three times power consumed when phase loads are connected in star.three-phase star connected load consumes 600 W from a three-phase balanced supply. Hence three-phase Delta connected load consumes 3 x 600 W = 1800 W from a three-phase balanced supply. 1800 W = 1.8 kWCorrect answer would be 1.8 kWLearn More:Show that power consumed by three identical phase loads ...brainly.in/question/6686827 |
|