A two bus system is shown below, If 150 MW is transmitted from plant 2 to the load, a transmission loss of 15 MW is incurred. The incremental fuel costs of the two plants are: dC1dPG1=0.04PG1+20Rs/MWhdC2dPG2=0.02PG2+16Rs/MWhThe power received by load is ____ MW. (Assume system λ = Rs. 25/MWh) 274.75

Answer» A two bus system is shown below,







If 150 MW is transmitted from plant 2 to the load, a transmission loss of 15 MW is incurred. The incremental fuel costs of the two plants are:



dC1dPG1=0.04PG1+20Rs/MWh



dC2dPG2=0.02PG2+16Rs/MWh



The power received by load is ____ MW. (Assume system λ = Rs. 25/MWh)
  1. 274.75