1.

An 11000/440 V, 50 Hz, 3-phase transformer is delta connected on the hv side and the lv windings are star connected. There should be 12 V per turn and the flux density is not to exceed 1.2 Wb/m2.The net cross sectional area of core in cm2 is _______.450.45

Answer» An 11000/440 V, 50 Hz, 3-phase transformer is delta connected on the hv side and the lv windings are star connected. There should be 12 V per turn and the flux density is not to exceed 1.2 Wb/m2.

The net cross sectional area of core in cm2 is _______.
  1. 450.45