1.

Given a single area with two generating units. Unit Rating Speed drop R (per unit on unit base) 1 400 0.04 2 800 0.05 The units share a load of P1=200MW,P2=500MW. The units are operating in parallel to share a load of 700 MW at 50 Hz frequency. The load is increased by 130 MW with B = 0, The value of new frequency caused by steady state frequency deviation is _______ Hz.49.75

Answer» Given a single area with two generating units.




















Unit Rating Speed drop R (per unit on unit base)
1 400 0.04
2 800 0.05



The units share a load of P1=200MW,P2=500MW. The units are operating in parallel to share a load of 700 MW at 50 Hz frequency. The load is increased by 130 MW with B = 0, The value of new frequency caused by steady state frequency deviation is _______ Hz.
  1. 49.75


Discussion

No Comment Found

Related InterviewSolutions