How To Use Level Tranasmitter In Closed Tank Application? |
|
Answer» In closed systems, the transmitter location is restricted by the maximum allowable distance above the lower tap. In pressurized systems, this is the same as the 1 atmosphere EQUIVALENT seen previously. In sub-atmospheric systems (vacuum systems), the transmitter should be mounted at or below the lower tap. This ensures the transmitter always SEES a positive pressure on both the measurement and the reference SIDES. In closed systems, the transmitter location is restricted by the maximum allowable distance above the lower tap. In pressurized systems, this is the same as the 1 atmosphere equivalent seen previously. In sub-atmospheric systems (vacuum systems), the transmitter should be mounted at or below the lower tap. This ensures the transmitter always sees a positive pressure on both the measurement and the reference sides. |
|