The main busbars in a generating station are divided into four section, each section being connected to a tie bar through a similar reactor. One 20 MVA, 11 kV generator having substransient reactance 20% is connected to each section bus bar. When a symmetrical fault takes place between the phases of one of the section busbar, the voltage on the remaining section falls to 65% of the normal value. The reactance of each reactors is _____ ohms.0.556

Answer» The main busbars in a generating station are divided into four section, each section being connected to a tie bar through a similar reactor. One 20 MVA, 11 kV generator having substransient reactance 20% is connected to each section bus bar. When a symmetrical fault takes place between the phases of one of the section busbar, the voltage on the remaining section falls to 65% of the normal value. The reactance of each reactors is _____ ohms.
  1. 0.556