The resistance and leakage reactance of a 10 kVA, 50 Hz, 2300/230 V distribution transformer are:r1=3.96 Ω, r2=0.0396 Ωx1=15.8 Ω, x2=0.158 ΩThe transformer delivers rated kVA at 0.8 p.f lagging to a load on LV side to maintain 230 V across load terminals. The HV side voltage is _________V. 2411.69 |
|
Answer» The resistance and leakage reactance of a 10 kVA, 50 Hz, 2300/230 V distribution transformer are: r1=3.96 Ω, r2=0.0396 Ω x1=15.8 Ω, x2=0.158 Ω The transformer delivers rated kVA at 0.8 p.f lagging to a load on LV side to maintain 230 V across load terminals. The HV side voltage is _________V.
|
|