What are important guidelines for conducting HV test? |
|
Answer» Based on the recommendations given in IS: 4029:1977 decided DC test voltage = (2E+1kV) 1.6 * M Where E = rated voltage. 2.6 = AC to DC conversion factor. M = derator factor which is a function to be decided on the basis of the age and condition of equipment. The DC voltage applied in steps and the leakage current recorded at each step. A plot leakage current Vs test voltage is to be plotted as the test progress. Some recommendations of IS : 4029 : 1977. a. The HV test made on the windings on acceptance shall as far as possible not be repeated. If however a second test to be made at 80% of the voltage given by the empirical formula given above. b. Test voltage for completely rewound motor = full test voltage for new motor. c. Partially rewound or overhauled motor = 75% * full test voltage for a new motor. d. Before the test for the old parts of the winding shall be carefully cleaned and dried. e. Before attempting of HV DC test a minimum PI value of motor should be obtained. |
|