What Are The Special Considerations When Measuring Ammonia?

Answer»

Tanks with anhydrous AMMONIA have a heavy vapor above the surface that attenuates the signal from the RADAR transmitter. A higher pressure in the tank will cause a more attenuated signal.

A special formula is therefore used to evaluate what the maximum measuring RANGE is in anhydrous ammonia as a function of the pressure in the tank.

For the 5600 the formula is:

Max Measuring Range (m) = 20 / Pressure in Bar

Note that, when measuring anhydrous (aqueous) ammonia, this formula does not apply. Hydrous ammonia has a HIGH dielectric constant and therefore provides good reflection.

Tanks with anhydrous ammonia have a heavy vapor above the surface that attenuates the signal from the radar transmitter. A higher pressure in the tank will cause a more attenuated signal.

A special formula is therefore used to evaluate what the maximum measuring range is in anhydrous ammonia as a function of the pressure in the tank.

For the 5600 the formula is:

Max Measuring Range (m) = 20 / Pressure in Bar

Note that, when measuring anhydrous (aqueous) ammonia, this formula does not apply. Hydrous ammonia has a high dielectric constant and therefore provides good reflection.