What Is The Difference Between X, Y & Z Purge Systems?
Answer»
X-rated purge SYSTEMSALLOW uncertified equipment to be installed in Zone 1 (Division 1). Usually, power to the enclosure is switched off if pressurization is lost.
Y-rated purge systems allow Zone 2 (Division 2) CERTIFIED equipment to be installed in Zone 1 (Division 1). Usually an ALARM sounds if pressurization is lost.
Z-rated purge SYSTEM allows uncertified equipment to be installed in Zone 2 (Division 2). Usually, an alarm sounds if pressurization is lost.