Will The Profibus Plugs With Diagnostic Leds Have Influence On The Busload? |
|
Answer» The input resistance of the DIAGNOSTIC PLUGS is approx. 1,5..2,0 MOhm (analog comparator input). This is 100 times higher as the RS 485 receiver input impedance. In theory this should not cause any problems which have not been DETECTED so far. The input resistance of the diagnostic plugs is approx. 1,5..2,0 MOhm (analog comparator input). This is 100 times higher as the RS 485 receiver input impedance. In theory this should not cause any problems which have not been detected so far. |
|