Explore topic-wise InterviewSolutions in .

This section includes InterviewSolutions, each offering curated multiple-choice questions to sharpen your knowledge and support exam preparation. Choose a topic below to get started.

51.

What Are The Methods Of Capacitive Switching?

Answer»

52.

What Do You Mean By Current Chopping?

Answer»

When interrupting low inductive currents such as magnetizing currents of the TRANSFORMER, shunt reactor, the rapid deionization of the contact space and blast effect MAY CAUSE the current to be interrupted before the natural current zero. This PHENOMENON of INTERRUPTION of the current before its natural zero is called current chopping.

When interrupting low inductive currents such as magnetizing currents of the transformer, shunt reactor, the rapid deionization of the contact space and blast effect may cause the current to be interrupted before the natural current zero. This phenomenon of interruption of the current before its natural zero is called current chopping.

53.

What Is Resistance Switching?

Answer»

It is the METHOD of connecting a resistance in PARALLEL with the contact space(arc). The resistance reduces the restriking voltage frequency and it diverts part of the arc current. It assists the CIRCUIT breaker in interrupting the MAGNETIZING current and capacity current.

It is the method of connecting a resistance in parallel with the contact space(arc). The resistance reduces the restriking voltage frequency and it diverts part of the arc current. It assists the circuit breaker in interrupting the magnetizing current and capacity current.

54.

What Are The Advantages Of Static Relay Over Electromagnetic Relay?

Answer»
  • Low power consumption as low as 1mW
  • No moving contacts; hence associated problems of arcing, contact bounce, erosion, replacement of contacts
  • No gravity effect on OPERATION of static relays. Hence can be used in vessels ie, ships, aircrafts etc.
  • A SINGLE relay can perform several functions like over current, under voltage, single phasing protection by incorporating respective functional blocks. This is not possible in ELECTROMAGNETIC relays
  • Static relay is compact
  • Superior operating characteristics and accuracy
  • Static relay can think , programmable operation is possible with static relay
  • Effect of vibration is nil, hence can be used in earthquake-prone areas o Simplified TESTING and servicing. Can convert even non-ELECTRICAL quantities to electrical in conjunction with transducers.

55.

What Is Cpmc?

Answer»

It is combined PROTECTION, monitoring and CONTROL SYSTEM INCORPORATED in the static system.

It is combined protection, monitoring and control system incorporated in the static system.

56.

What Is A Programmable Relay?

Answer»

A STATIC RELAY may have one or more programmable units such as microprocessors or MICROCOMPUTERS in its CIRCUIT.

A static relay may have one or more programmable units such as microprocessors or microcomputers in its circuit.

57.

What Is Power Swing?

Answer»

During SWITCHING of lines or wrong synchronization SURGES of real and reactive power flowing in TRANSMISSION line causes severe oscillations in the VOLTAGE and current vectors. It is represented by curves originating in load regions and TRAVELING towards relay characteristics.

During switching of lines or wrong synchronization surges of real and reactive power flowing in transmission line causes severe oscillations in the voltage and current vectors. It is represented by curves originating in load regions and traveling towards relay characteristics.

58.

What Is Static Relay?

Answer»

It is a RELAY in which measurement or COMPARISON of electrical QUANTITIES is made in a STATIC network which is DESIGNED to give an output signal when a threshold condition is passed which operates a tripping device.

It is a relay in which measurement or comparison of electrical quantities is made in a static network which is designed to give an output signal when a threshold condition is passed which operates a tripping device.

59.

What Are The Problems In Bus Zone Differential Protection?

Answer»
  1. Large number of circuits, DIFFERENT current levels for different circuits for external faults.
  2. Saturation of CT CORES due to dc component and ac component in short circuit CURRENTS. The saturation introduces ratio error.
  3. Sectionalizing of the bus makes circuit complicated.
  4. Setting of relays need a CHANGE with large LOAD changes.

60.

What Are The Causes Of Bus Zone Faults?

Answer»
  • Failure of support INSULATOR resulting in earth fault
  • FLASHOVER across support insulator during over VOLTAGE Heavily polluted insulator causing flashover EARTHQUAKE, mechanical damage etc.

61.

What Is Field Suppression?

Answer»

When a fault occurs in an alternator winding EVEN though the generator circuit breaker is tripped, the fault continues to fed because EMF is induced in the generator itself. Hence the field circuit breaker is opened and STORED energy in the field winding is DISCHARGED through another resistor. This method is known as field SUPPRESSION.

When a fault occurs in an alternator winding even though the generator circuit breaker is tripped, the fault continues to fed because EMF is induced in the generator itself. Hence the field circuit breaker is opened and stored energy in the field winding is discharged through another resistor. This method is known as field suppression.

62.

What Are The Errors In Ct?

Answer»

RATIO ERROR

PERCENTAGE ratio error = [(Nominal ratio – Actual ratio)/Actual ratio] x 100 The value of transformation ratio is not equal to the TURNS ratio.

Phase angle error:

Phase angle =180/π[(ImCos δ-I1Sin δ)/NIS]

Ratio error

Percentage ratio error = [(Nominal ratio – Actual ratio)/Actual ratio] x 100 The value of transformation ratio is not equal to the turns ratio.

Phase angle error:

Phase angle =180/π[(ImCos δ-I1Sin δ)/nIs]

63.

What Are The Merits Of Carrier Current Protection?

Answer»

FAST OPERATION, AUTO re-closing POSSIBLE, easy discrimination of SIMULTANEOUS faults .

Fast operation, auto re-closing possible, easy discrimination of simultaneous faults .

64.

Why Busbar Protection Is Needed?

Answer»

Fault level at busbar is high.

The STABILITY of the SYSTEM is affected by the faults in the bus zone.

A fault in the bus bar causes interruption of SUPPLY to a large PORTION of the system network.

Fault level at busbar is high.

The stability of the system is affected by the faults in the bus zone.

A fault in the bus bar causes interruption of supply to a large portion of the system network.

65.

What Is Over Fluxing Protection In Transformer?

Answer»

If the TURNS ratio of the TRANSFORMER is more than 1:1, there will be HIGHER CORE loss and the capability of the transformer to withstand this is limited to a few minutes only. This phenomenon is CALLED over fluxing.

If the turns ratio of the transformer is more than 1:1, there will be higher core loss and the capability of the transformer to withstand this is limited to a few minutes only. This phenomenon is called over fluxing.

66.

What Is Ref Relay?

Answer»

It is RESTRICTED earth fault RELAY. When the fault occurs very near to the neutral point of the transformer, the voltage available to drive the earth circuit is very small, which may not be sufficient to activate the relay, unless the relay is set for a very low CURRENT. Hence the zone of protection in the WINDING of the transformer is restricted to cover only around 85%. Hence the relay is called REF relay.

It is restricted earth fault relay. When the fault occurs very near to the neutral point of the transformer, the voltage available to drive the earth circuit is very small, which may not be sufficient to activate the relay, unless the relay is set for a very low current. Hence the zone of protection in the winding of the transformer is restricted to cover only around 85%. Hence the relay is called REF relay.

67.

What Are The Problems Arising In Differential Protection In Power Transformer And How Are They Overcome?

Answer»

DIFFERENCE in lengths of pilot wires on EITHER sides of the relay. This is overcome by connecting adjustable resistors to pilot wires to get equipotential points on the pilot wires.

Difference in CT ratio error difference at high values of short circuit currents that makes the relay to operate even for external or through faults. This is overcome by introducing bias coil.

Tap changing alters the ratio of voltage and currents between HV and LV sides and the relay will sense this and act. Bias coil will solve this.

Magnetizing inrush current appears wherever a transformer is energized on its primary side PRODUCING harmonics. No current will be seen by the secondary. CT’s as there is no load in the circuit. This difference in current will actuate the differential relay. A harmonic restraining unit is added to the relay which will BLOCK it when the transformer is energized.

Difference in lengths of pilot wires on either sides of the relay. This is overcome by connecting adjustable resistors to pilot wires to get equipotential points on the pilot wires.

Difference in CT ratio error difference at high values of short circuit currents that makes the relay to operate even for external or through faults. This is overcome by introducing bias coil.

Tap changing alters the ratio of voltage and currents between HV and LV sides and the relay will sense this and act. Bias coil will solve this.

Magnetizing inrush current appears wherever a transformer is energized on its primary side producing harmonics. No current will be seen by the secondary. CT’s as there is no load in the circuit. This difference in current will actuate the differential relay. A harmonic restraining unit is added to the relay which will block it when the transformer is energized.

68.

What Are The Limitations Of Buchholz Relay?

Answer»

Only FAULT below the oil level are detected.

Mercury switch setting should be very accurate, otherwise even for vibration, there can be a FALSE operation.

The relay is of SLOW OPERATING type, which is unsatisfactory.

Only fault below the oil level are detected.

Mercury switch setting should be very accurate, otherwise even for vibration, there can be a false operation.

The relay is of slow operating type, which is unsatisfactory.

69.

What Are The Main Safety Devices Available With Transformer?

Answer»

OIL level GUAGE, sudden pressure DELAY, oil TEMPERATURE indicator, WINDING temperature indicator .

Oil level guage, sudden pressure delay, oil temperature indicator, winding temperature indicator .

70.

What Is The Backup Protection Available For An Alternator? Overcurrent And Earth Fault Protection Is The Backup Protections. What Are Faults Associated With An Alternator?

Answer»

External fault or through fault

Internal fault

1. SHORT circuit in transformer WINDING and CONNECTION

2.Incipient or slow DEVELOPING FAULTS

External fault or through fault

Internal fault

1. Short circuit in transformer winding and connection

2.Incipient or slow developing faults

71.

Why Neutral Resistor Is Added Between Neutral And Earth Of An Alternator?

Answer»

In order to LIMIT the flow of CURRENT through NEUTRAL and earth a resistor is introduced between them.

In order to limit the flow of current through neutral and earth a resistor is introduced between them.

72.

What Are The Uses Of Buchholz’s Relay?

Answer»

Bucholz relay is used to give an alarm in case of incipient( slow-developing) FAULTS in the TRANSFORMER and to connect the transformer from the supply in the event of severe INTERNAL faults. It is USUALLY used in oil immersion transformers with a RATING over 750KVA.

Bucholz relay is used to give an alarm in case of incipient( slow-developing) faults in the transformer and to connect the transformer from the supply in the event of severe internal faults. It is usually used in oil immersion transformers with a rating over 750KVA.

73.

Give The Limitations Of Merz Price Protection?

Answer»

Since neutral earthing resistances are often used to protect circuit from earth-fault currents, it becomes IMPOSSIBLE to protect the whole of a star-connected alternator. If an earth-fault occurs near the neutral point, the voltage may be INSUFFICIENT to operate the relay. Also it is extremely difficult to find two identical CT’s. In addition to this, there always an inherent phase difference between the primary and the secondary QUANTITIES and a possibility of current through the relay EVEN when there is no fault.

Since neutral earthing resistances are often used to protect circuit from earth-fault currents, it becomes impossible to protect the whole of a star-connected alternator. If an earth-fault occurs near the neutral point, the voltage may be insufficient to operate the relay. Also it is extremely difficult to find two identical CT’s. In addition to this, there always an inherent phase difference between the primary and the secondary quantities and a possibility of current through the relay even when there is no fault.

74.

What Are The Main Types Of Stator Winding Faults?

Answer»

FAULT between phase and GROUND; fault between PHASES and inter-turn fault INVOLVING turns of the same phase WINDING.

Fault between phase and ground; fault between phases and inter-turn fault involving turns of the same phase winding.

75.

What Are The Features Of Directional Relay?

Answer»

HIGH speed OPERATION; high sensitivity; ability to operate at low voltages; adequate short-time THERMAL ratio; burden MUST not be excessive.

High speed operation; high sensitivity; ability to operate at low voltages; adequate short-time thermal ratio; burden must not be excessive.

76.

Mention Any Two Disadvantage Of Carrier Current Scheme For Transmission Line Only.

Answer»

The PROGRAM time (ie, the time taken by the carrier to reach the other end-upto .1% mile); the RESPONSE time of BAND pass filter; capacitance phase-shift of the TRANSMISSION line .

The program time (ie, the time taken by the carrier to reach the other end-upto .1% mile); the response time of band pass filter; capacitance phase-shift of the transmission line .

77.

Define The Term Pilot With Reference To Power Line Protection.

Answer»

Pilot WIRES refers to the wires that connect the CT’s placed at the ends of a POWER transmission line as part of its PROTECTION SCHEME. The resistance of the pilot wires is usually LESS than 500 ohms.

Pilot wires refers to the wires that connect the CT’s placed at the ends of a power transmission line as part of its protection scheme. The resistance of the pilot wires is usually less than 500 ohms.

78.

What Is An Under Frequency Relay?

Answer»

An under frequency RELAY is one which operates when the frequency of the SYSTEM (usually an ALTERNATOR or transformer) falls below a CERTAIN value.

An under frequency relay is one which operates when the frequency of the system (usually an alternator or transformer) falls below a certain value.

79.

What Are The Various Faults To Which A Turbo Alternator Is Likely To Be Subjected? failure Of Steam Supply; Failure Of Speed; Overcurrent; Over Voltage; Unbalanced

Answer»

LOADING; STATOR WINDING FAULT 

loading; stator winding fault 

80.

Mention The Short Comings Of Merz Price Scheme Of Protection Applied To A Power Transformer?

Answer»

In a POWER transformer, currents in the PRIMARY and secondary are to be compared. As these two currents are usually different, the use of identical transformers will give differential current, and operate the relay under no-load condition. Also, there is usually a PHASE difference between the primary and secondary currents of three phase transformers. Even CT’s of PROPER turn-ratio are used, the differential current may FLOW through the relay under normal condition.

In a power transformer, currents in the primary and secondary are to be compared. As these two currents are usually different, the use of identical transformers will give differential current, and operate the relay under no-load condition. Also, there is usually a phase difference between the primary and secondary currents of three phase transformers. Even CT’s of proper turn-ratio are used, the differential current may flow through the relay under normal condition.

81.

What Is The Need Of Relay Coordination?

Answer»

The operation of a relay should be fast and selective, ie, it should isolate the fault in the shortest possible time causing minimum disturbance to the SYSTEM. Also, if a relay fails to operate, there should be SUFFICIENTLY quick BACKUP protection so that the REST of the system is protected. By COORDINATING relays, faults can always be isolated quickly without serious disturbance to the rest of the system.

The operation of a relay should be fast and selective, ie, it should isolate the fault in the shortest possible time causing minimum disturbance to the system. Also, if a relay fails to operate, there should be sufficiently quick backup protection so that the rest of the system is protected. By coordinating relays, faults can always be isolated quickly without serious disturbance to the rest of the system.

82.

What Is Biased Differential Bus Zone Reduction?

Answer»

The biased beam relay is designed to respond to the differential current in TERMS of its fractional relation to the current flowing through the PROTECTED zone. It is essentially an over-current BALANCED beam relay type with an ADDITIONAL RESTRAINING coil. The restraining coil produces a bias force in the opposite direction to the operating force.

The biased beam relay is designed to respond to the differential current in terms of its fractional relation to the current flowing through the protected zone. It is essentially an over-current balanced beam relay type with an additional restraining coil. The restraining coil produces a bias force in the opposite direction to the operating force.

83.

Mention Any Two Applications Of Differential Relay?

Answer»

PROTECTION of GENERATOR & generator transformer UNIT; protection of large MOTORS and busbars .

Protection of generator & generator transformer unit; protection of large motors and busbars .

84.

What Are Over And Under Current Relays?

Answer»

Overcurrent relays are those that operate when the CURRENT in a line exceeds a predetermined VALUE. (eg: INDUCTION TYPE non-directional/directional overcurrent relay, differential overcurrent relay)whereas undercurrent relays are those which operate whenever the current in a circuit/line drops below a predetermined value.(eg: differential over-voltage relay)

Overcurrent relays are those that operate when the current in a line exceeds a predetermined value. (eg: Induction type non-directional/directional overcurrent relay, differential overcurrent relay)whereas undercurrent relays are those which operate whenever the current in a circuit/line drops below a predetermined value.(eg: differential over-voltage relay)

85.

Define Resetting Time Of A Relay?

Answer»

It is defined as the time TAKEN by the relay from the instant of isolating the FAULT to the MOMENT when the fault is REMOVED and the relay can be reset.

It is defined as the time taken by the relay from the instant of isolating the fault to the moment when the fault is removed and the relay can be reset.

86.

Define Operating Time Of A Relay?

Answer»

It is DEFINED as the time PERIOD extended from the occurrence of the fault through the RELAY DETECTING the fault to the operation of the relay.

It is defined as the time period extended from the occurrence of the fault through the relay detecting the fault to the operation of the relay.

87.

Define Energizing Quantity?

Answer»

It REFERS to the CURRENT or voltage which is USED to activate the relay into OPERATION.

It refers to the current or voltage which is used to activate the relay into operation.

88.

Name The Different Kinds Of Over Current Relays?

Answer»

INDUCTION type non-DIRECTIONAL over CURRENT RELAY,Induction type directional over current relay & current differential relay.

Induction type non-directional over current relay,Induction type directional over current relay & current differential relay.

89.

What Is Back Up Protection?

Answer»

Is the second LINE of defence , which OPERATES if the primary PROTECTION FAILS to activate within a definite time delay.

Is the second line of defence , which operates if the primary protection fails to activate within a definite time delay.

90.

What Is Primary Protection?

Answer»

Is the PROTECTION in which the FAULT OCCURRING in a line will be CLEARED by its own relay and circuit breaker.It serves as the first line of defence.

Is the protection in which the fault occurring in a line will be cleared by its own relay and circuit breaker.It serves as the first line of defence.

91.

What Are Unit System And Non Unit System?

Answer»

A unit protective system is ONE in which only faults OCCURRING within its protected ZONE are isolated.Faults occurring elsewhere in the system have no influence on the operation of a unit system.A NON unit system is a protective system which is activated EVEN when the faults are external to its protected zone.

A unit protective system is one in which only faults occurring within its protected zone are isolated.Faults occurring elsewhere in the system have no influence on the operation of a unit system.A non unit system is a protective system which is activated even when the faults are external to its protected zone.

92.

Define Protected Zone?

Answer»

Are those which are directly protected by a protective SYSTEM such as RELAYS, FUSES or switchgears.If a fault occurring in a zone can be immediately detected and or isolated by a protection scheme DEDICATED to that particular zone.

Are those which are directly protected by a protective system such as relays, fuses or switchgears.If a fault occurring in a zone can be immediately detected and or isolated by a protection scheme dedicated to that particular zone.

93.

Give The Consequences Of Short Circuit?

Answer»

Whenever a short-circuit OCCURS, the current flowing through the coil increases to an enormous value. If protective relays are present , a HEAVY current also flows through the relay coil, causing it to operate by CLOSING its contacts.The trip circuit is then closed , the circuit breaker opens and the fault is ISOLATED from the REST of the system. Also, a low voltage may be created which may damage systems connected to the supply.

Whenever a short-circuit occurs, the current flowing through the coil increases to an enormous value. If protective relays are present , a heavy current also flows through the relay coil, causing it to operate by closing its contacts.The trip circuit is then closed , the circuit breaker opens and the fault is isolated from the rest of the system. Also, a low voltage may be created which may damage systems connected to the supply.

94.

What Are The Functions Of Protective Relays?

Answer»

ANSWER :To detect the FAULT and initiate the operation of the circuit breaker to isolate the defective element from the rest of the system, THEREBY protecting the system from damages CONSEQUENT to the fault.