

InterviewSolution
Saved Bookmarks
1. |
A single-phase load is connected between R and Y terminals of a 220 V, symmetrical, 3-phase, 4 wire systems with phase sequence RYB. A watt-meter is connected in the system. The watt-meter will read (pf = 0.8 lagging)?(a) – 795 W(b) – 168 W(c) + 597 W(d) + 795 WI have been asked this question in homework.I want to ask this question from Advanced Problems on Measurement of Power in Polyphase Circuit in chapter Measurement of Power and Related Parameters of Electrical Measurements |
Answer» The CORRECT CHOICE is (b) – 168 W |
|