1.

An Operator Tells You That Flow Indication Is More? How Would You Start Checking?

Answer»
  1. First flushing the transmitter. Flush both the impulse lines. Adjust the ZERO by equalizing if NECESSARY. If still the INDICATION is more then.
  2. CHECK L.P. side for choke. If that is clean then.
  3. Check the LEAKS on L.P. side. If not.
  4. Calibrate the transmitter.



Discussion

No Comment Found