How 6.6 kV-bus supply was chosen? 

Answer»

11 kV was rejected in view of the high insulation cost with 11 kV motors. 3.3 kV was rejected, since max motor size with 3.3 kV bus is limited to 2 MW. But we are having the motors having rating more than 2 MW, which cannot suit to 3.3 kV bus. 6.6 kV bus we can start upto 5 mw size motor. 