Why 2 types of earth fault relays in 6.6 kV side of transformers? |
|
Answer» I – Trips 6.6 kV breakers only. It gives primary protection for 6.6 kV bus bars. I1 – Trips the both HT and LT breakers. It acts as a backup to ref and also acts as backup to bus bar earthfault relay. |
|