Why Does My Valve Actuate/open Early? |
|
Answer» It MAY not be. Warn/simmer or seat leakage is sometimes mistaken for set pressure. Visible or audible leakage or system pressure drop is not set pressure. The correct DEFINITION of set pressure is:For liquid service, first vertical steady stream. For liquid service, first vertical steady stream. For some VALVES in air/gas service, First audible. Variance of set pressure is ALLOWED, i.e., a Section VIII air valve with a nameplate of 100 psig set pressure may open from 97 psig to 103 psig, but will be factory set around 102 psig. It may not be. Warn/simmer or seat leakage is sometimes mistaken for set pressure. Visible or audible leakage or system pressure drop is not set pressure. The correct definition of set pressure is:For liquid service, first vertical steady stream. For liquid service, first vertical steady stream. For some valves in air/gas service, First audible. Variance of set pressure is allowed, i.e., a Section VIII air valve with a nameplate of 100 psig set pressure may open from 97 psig to 103 psig, but will be factory set around 102 psig. |
|