Why resistance grounding preferred for less than 33 kV and more than 415 V? |
|
Answer» a) To limit the earth fault current for equipment safety else, high short ckt forces dislocate in windings/bus bars etc, b) Over voltage due to arcing ground reduced c) Permits earth fault protection (not possible in ungrounded system) |
|