1. |
A 3-phase power system is represented by one line diagram as shown in the figure below: The ratings of equipments are the following: Genrator (G) : 15 MVA, 6.6 kV, X1 = 15%,X2 = 10%Transformer : 15 MVA, 6.6 kV delta/33 kV star,X1=X2=X0=6%Line reactance : X1=X2=2Ω and X0=6ΩIf a SLG fault occurs on bus bar B, then the fault current is _______ p.u.0 |
Answer» A 3-phase power system is represented by one line diagram as shown in the figure below:![]() The ratings of equipments are the following: Genrator (G) : 15 MVA, 6.6 kV, X1 = 15%, X2 = 10% Transformer : 15 MVA, 6.6 kV delta/33 kV star, X1=X2=X0=6% Line reactance : X1=X2=2Ω and X0=6Ω If a SLG fault occurs on bus bar B, then the fault current is _______ p.u.
|
|