A 30 MVA, 3-phase, 50 Hz, 13.8 kV, star-connected synchronous generator has positive, negative and zero sequence reactances, 15%, 15% and 5% respectively. A reactance (Xn) is connected between the neutral of the generator and ground. A double line to ground fault takes place involving phase 'b' and 'c' with a fault impendance of j0.1 p.u.. The value of xn(in p.u.) that will limit the positive sequence generator current to 4270 A is 1.07 |
Answer» A 30 MVA, 3-phase, 50 Hz, 13.8 kV, star-connected synchronous generator has positive, negative and zero sequence reactances, 15%, 15% and 5% respectively. A reactance (Xn) is connected between the neutral of the generator and ground. A double line to ground fault takes place involving phase 'b' and 'c' with a fault impendance of j0.1 p.u.. The value of xn(in p.u.) that will limit the positive sequence generator current to 4270 A is
|
|