1.

A cylindrical rotor synchronous generator has steady state synchronous reactance of 0.7 pu and subtransient reactance of 0.2 pu. It is operating at (1+ j0) pu terminal voltage with an internal emf of (1 + j0.7)pu. Following a three-phase solid short circuit fault at the terminal of the generator, the magnitude of the subtransient internal emf in p.u (rounded off to 2 decimal places) is 1.02

Answer» A cylindrical rotor synchronous generator has steady state synchronous reactance of 0.7 pu and subtransient reactance of 0.2 pu. It is operating at (1+ j0) pu terminal voltage with an internal emf of (1 + j0.7)pu. Following a three-phase solid short circuit fault at the terminal of the generator, the magnitude of the subtransient internal emf in p.u (rounded off to 2 decimal places) is
  1. 1.02